INCREASING CAPACITY OF ANTENNA SUPPORT STRUCTURES

 

 

BACKGROUND

 

Telecommunication towers have traditionally been designed for single carrier occupancy, with little or no allowance for future expansion requirements.

 

There has been a growing tendency for municipalities or other regulatory bodies to oppose building of new structures, especially in residential areas. Also it makes more economic sense to place antennas at a desired height on an existing tower.

 

 

TOWER REINFORCING CHECKLIST

 

ü      Do you have all the tower design details (installation drawings, part drawings, foundation design, soil reports, materials used)?

 

ü      What is the design standard the tower was designed to? Was the design adequate then with the existing and future antenna and transmission line loading? It is important to establish the structural adequacy of the tower at the time when it was designed. You don't want to be responsible for reinforcing work for a tower that was under-designed. Did the tower have any capacity left? Were the member connections designed to the maximum loads in members or to member capacities? It is common practice that connections to be designed to member capacities, to allow for future increases in loads.

 

ü      What is the current capacity of the tower? National standards are updated every five years or so. Tower design standards reflect the state of the art knowledge at a particular time. Older standards might have been more conservative with the wind loading and member capacities. However, there are components of the towers that will have their design capacity reduced as a result of past performance of components in the same class.

ü      For example, the caisson foundations have their capacity reduced almost to 50% with the new update of the CSA-S37 Canadian standard in 2001. Diagonal members in cross-braced panels have their capacity considerably reduced from the 1986 to 1994 editions of the CSA-S37 standard to have it increased in the 2001 update.


 

ü      If there is no change in the loading of the tower, generally there is no need to analyze the tower when new standards come into force. However any modification in the equipment loading (antennas, transmission lines, etc.) will require a structural assessment. Modifications in the equipment loading do not necessarily mean addition of new equipment. Removal of equipment can have a deleterious effect on some structures, particularly guyed towers.

 

ü      Is the analysis method used the most appropriate? There is a variation in the analysis methods employed by various tower designers and consultants. Some of the simplified methods, like modeling a tower as cantilever beam or a continuous supported beam might be more conservative but they might be missing some secondary effects on the towers. Finite element methods where every tower member is modeled are preferred. Loading modeling is critical, too. Exact positioning of the antenna lines will model the loading more accurately as shielding between lines and structural members is considered.

 

ü      The more sophisticated the analysis method is the more accurate picture of the actual state of the tower is. Simplified methods might be adequate for the tower initial design but when the tower is analyzed in the as-built condition a more sophisticated analysis is required.

 

ü      Does the model reflect accurately the as-built condition of the tower? This is very important especially for loading. Relying only on the original tower drawings might not be the answer. Tower antenna mapping is required especially for transmission line positioning on the tower faces or legs.

 

ü      Is there physical room for the addition of the proposed antennas and transmission lines at the desired height? If it is a monopole is there room in the existing entry and exit ports for the additional cables? Do you require new ports? If new ports are required then a structural analysis of the monopole section with the additional port is required.

 

ü      What are the critical components of the structure? What are the weakest points? Some components can be easily upgraded (replacing a diagonal member of a lattice tower with a stronger member), while others are very costly to upgrade (foundations in uplift).

 

ü      What reinforcing options are available? The following section will describe the most common reinforcing solutions. For example, bolting or clamping on an existing member is preferable to welding on site.

 

ü      What is the likely cost of tower reinforcing? Technically any tower can be reinforced short of building another structure around it but economically might not be feasible, as it will cost more than a new structure.

 

ü      What is the timescale of tower reinforcing?

 

These questions need to be answered to ensure a successful tower reinforcing.

 

 

 

REINFORCEMENT SOLUTIONS

 

Tower Type

Description of Problem

Member Type

Reinforcement Solution

 

 

 

 

Self-support

Moderate leg buckling overstress

Angle

Mid-panel horizontals

 

 

Pipe

Mid-panel horizontals

 

 

Solid Round

Mid-panel horizontals

 

 

Lattice

Mid-panel horizontals

 

Severe leg buckling overstress

Angle

Bolted-on flat bars

 

 

Pipe

Material welded

 

 

Solid Round

Material welded

 

 

Lattice

Material welded

 

Diagonal bolt overstress

Angle

Bolt replacement

 

 

Angle

Back to back diagonal (double shear)

 

Diagonal compression overstress

Angle

Add secondary members

 

 

Angle

Angle replacement

 

 

Angle

Back to back diagonal

 

 

Solid Round

Add secondary members

 

 

Solid Round

Increase radius of gyration with bolted-on angles

 

Diagonal tension overstress (bolts edge distance)

Angle

Back to back diagonal

 

Anchor Bolts Overstress

 

Additional Anchor Bolts

 

 

 

Legs Unloading

 

 

 

 

Guyed Tower

Moderate leg buckling overstress

Angle

Mid-panel horizontals

 

 

Pipe

Mid-panel horizontals

 

 

Solid Round

Mid-panel horizontals

 

Severe leg buckling overstress

Angle

Bolted-on flat bars

 

 

Pipe

Material welded

 

 

Solid Round

Material welded

 

Diagonal Compression Overstress

Solid Round

Add secondary members

 

 

Solid Round

Increase radius of gyration with bolted-on angles

 

 

Solid Round

Change bracing pattern (single braced to cross-braced)

 

 

Angle

Add secondary members

 

 

Angle

Angle replacement

 

 

Angle

Back to back diagonal

 

Minor guys overstresses

Guy cables

Decrease initial tension

 

Moderate guys overstresses

Guy cables

Increase initial tension to adjacent guy cable elevations

 

Moderate and severe guys overstresses

Guy cables

Guy cables replacement

 

 

 

 

Monopole

Shell Overstress

Shell

Bolt-on material

 

Shell Overstress

Shell

Adding guy cables and anchors

 

Anchor bolts overstress

Anchor bolts

New anchor bolts

 

Anchor bolts overstress

Anchor bolts

Support extensions to decrease load

 

 

 

 


Pad and Pier

Bearing Overstress

Pad

Pad extension (dowels) - new concrete

 

Insufficient Uplift Capacity

Pad

Pad extension (dowels) - new concrete

 

Insufficient Uplift Capacity

Pad and Pier

Joining together the piers with reinforced concrete beams

 

Insufficient Moment Capacity

Pier

Pier Extension - new concrete

 

 

 

 

Raft

Bearing Overstress

Raft

Raft extension (dowels) - new concrete

 

Overturning moment

Raft

Raft extension (dowels) - new concrete

 

 

 

 

Dead-man

Pullout

Dead-man

Adding berm

 

Severe pullout

Dead-man

Some of the guy cables relocated to new dead-man anchor to relieve loads.

 

 

 

RISKS

 

Some of the structures, especially guyed towers might experience loads close to capacity even in absence of wind conditions. While reinforcing towers, some of the members might need to be taken out and replaced. When member replacement is required then temporary supports must be installed. Reinforcing work should be carried out in good weather with little or no wind.

 

Excavating around a foundation decreases significantly the uplift or pullout resistance.  

 

 

 

CONCLUSIONS

 

It is more economical to allow for a multi-carrier occupancy when tower are initially designed. However, if reinforcing is required, then good Engineering can make the difference between a money-saving solution, easy to implement and a non-feasible solution.

 